Zambia site power: is 250 kVA enough?
Ahmed Ben Salah
Verified member · Service engineer
Site power from a 250 kVA set; tower crane 45 kW, batching plant 60 kW.
With lighting and offices at peak, breakers trip and engine speed drops.
Is capacity short, or is it starting current? How do we calculate?
Discussion (3)
Chanda M.Verified member · Service engineer2026-10-08
Simultaneous starting draws up to three times rated current; with that diversity, 250 kVA is genuinely tight.
Kwame A.Verified member · Mine equipment manager2026-10-09
Add soft starters or staged starting first; it costs less than a new set and explains many trips.
Paulo M.Verified member · Project chief engineer2026-10-10
Keep 25% margin as a rule so later additions do not overload it.